Academics – Electro-Technology : 2016/DEC/05
Question
Q5. (a) State two disadvantages of operating electrical circuits at a low power factor.
(b) a 3-ph, 440V, 80 kVA transformers supply a unity power factor load of 15 kW and an inductive load of 55 kw and power factor of 0.67. Determine the minimum kVAR rating of a load capacitor bank to ensure that the supply transformer is not overloaded.
Calculate the current supplied by the transformer in EACH pf the following;
(i) Prior to the power factor correction being applied;
(ii) After the power factor correction is applied.
Asked in Year/Month/Ques No.
Hello Guest User,
Answers are available via our app only.
Please buy a membership plan and login via our app to view answers.
Please buy a membership plan and login via our app to view answers.